D!NNy
Senior Member
- Location
- San Luis Obispo
I have 350MCM 600V THHN cable pulled in a 3" rmc conduit via a Pull box / junction box
Ambiance is ocean area (corrosive)
Based on 314.28
Straight pull
- with out splicing min length of JB/PB is 24"
- with splicing min length of JB/PB is 18"
JB/PB of 18" * 18" * 8" is already purchased
options for splcing:
1. PDB, however per 314.28 (E) 2, min manufacturer recommended size is 24". also
Are there any other options for splicing that code compliance, UL rated, and can use the 18" boxes .
3M has this product: https://rexel-cdn.com/Products/3M/5304.pdf?i=6AA11246-243B-4660-B2EB-A5F7A2BB1A63
Polaris has this product : https://rexel-cdn.com/Products/NSITork/ISR-500.pdf?i=CAD229D7-9F3E-4A4B-AD3E-D4714BC888A9
Thanks for the help in advance
Ambiance is ocean area (corrosive)
Based on 314.28
Straight pull
- with out splicing min length of JB/PB is 24"
- with splicing min length of JB/PB is 18"
JB/PB of 18" * 18" * 8" is already purchased
options for splcing:
1. PDB, however per 314.28 (E) 2, min manufacturer recommended size is 24". also
Are there any other options for splicing that code compliance, UL rated, and can use the 18" boxes .
3M has this product: https://rexel-cdn.com/Products/3M/5304.pdf?i=6AA11246-243B-4660-B2EB-A5F7A2BB1A63
Polaris has this product : https://rexel-cdn.com/Products/NSITork/ISR-500.pdf?i=CAD229D7-9F3E-4A4B-AD3E-D4714BC888A9
Thanks for the help in advance