I have 350MCM 600V THHN cable pulled in a 3" rmc conduit via a Pull box / junction box
Ambiance is ocean area (corrosive)

Based on 314.28
Straight pull
- with out splicing min length of JB/PB is 24"
- with splicing min length of JB/PB is 18"

JB/PB of 18" * 18" * 8" is already purchased

options for splcing:
1. PDB, however per 314.28 (E) 2, min manufacturer recommended size is 24". also

Are there any other options for splicing that code compliance, UL rated, and can use the 18" boxes .

3M has this product: https://rexel-cdn.com/Products/3M/5304.pdf?i=6AA11246-243B-4660-B2EB-A5F7A2BB1A63
Polaris has this product : https://rexel-cdn.com/Products/NSITork/ISR-500.pdf?i=CAD229D7-9F3E-4A4B-AD3E-D4714BC888A9

Thanks for the help in advance
 
While the code permits a smaller enclosure where splicing, it is my opinion that it really needs to be larger than what is required for a straight pull without a splice.

You may be able to fit compression sleeves with heat shrink insulation in the 18x18" box, but you don't have a lot of room to work with.
 
I have 350MCM 600V THHN cable pulled in a 3" rmc conduit via a Pull box / junction box
Ambiance is ocean area (corrosive)

Based on 314.28
Straight pull
- with out splicing min length of JB/PB is 24"
- with splicing min length of JB/PB is 18"

JB/PB of 18" * 18" * 8" is already purchased

options for splcing:
1. PDB, however per 314.28 (E) 2, min manufacturer recommended size is 24". also

Are there any other options for splicing that code compliance, UL rated, and can use the 18" boxes .

3M has this product: https://rexel-cdn.com/Products/3M/5304.pdf?i=6AA11246-243B-4660-B2EB-A5F7A2BB1A63
Polaris has this product : https://rexel-cdn.com/Products/NSITork/ISR-500.pdf?i=CAD229D7-9F3E-4A4B-AD3E-D4714BC888A9

Thanks for the help in advance

manufacturer's recommendations do not carry the same weight as manufacturer's requirements.
 
where did you get the mfg rec min 24" from?

314.28.E.2 applies to a power distribution block
what you are doing is splicing, 1 cable in and 1 out, no taps or distribution

the polaris pg 1 isr look like a good choice
 
I found going the minimum often takes longer for the men and the"savings" is eaten by the labor.
 
I would never use an 18" box for splicing 350's. #2's yes, 350's a BIG no!

Over here we'd be using 24+" min and depending on the chosen splicing method and available space, more than likely larger than that. I don't know any electricians that like beating their hands up on the side of the box forcing oversized wires in too-small-of-a-box.
 