We're reusing some armor cable from one of our other plants and it will need to be spliced somewhere in the middle.
This is a parallel 500MCM feed (two armor cables) so both cables get spliced in the middle.
The contractor recommends that both feeders get spliced in the same box and that both sets of leads get tied together in the box (e.g. phase "A" gets tied to the other phase "A").
Personally this sounds like a dumb idea but I can't seem to find where it is not allowed in the NEC.
I'm aware of the other rules:
? They must be the same length
? They must be terminated in the same manner
? They must have the same conductor material
? They must be the same size in circular mil area
? They must have the same insulation type
but is tying them together in the middle specifically disallowed?
Thanks,
John
This is a parallel 500MCM feed (two armor cables) so both cables get spliced in the middle.
The contractor recommends that both feeders get spliced in the same box and that both sets of leads get tied together in the box (e.g. phase "A" gets tied to the other phase "A").
Personally this sounds like a dumb idea but I can't seem to find where it is not allowed in the NEC.
I'm aware of the other rules:
? They must be the same length
? They must be terminated in the same manner
? They must have the same conductor material
? They must be the same size in circular mil area
? They must have the same insulation type
but is tying them together in the middle specifically disallowed?
Thanks,
John