Splicing Rules

Status
Not open for further replies.

United36

Member
We are replacing older rooftop ac equipment with newer smaller equipment. The existing conductor to the older equipment is a 4/0 and the new equipment can only take up to a #2. So we are looking at using a burndy compression fitting to reduce to the smaller wire size. I can't find any code related issues regarding this but reducing the wire size dramatically like this seems odd. The splice would be in a new junction box about 20 feet away from the new unit and this is a dedicated circuit. Does anyone know of any issues that would come of this or code issues to be aware of?
 
what about using these terminal plugs? would save you from having to set a J box and splice.

029090.JPG
 
Does Burndy make a compression barrel splice that covers the range of conductors?

i don't know if Burndy does, but Panduit has a line of barrel type splices that have a very large range.

I have also been told that the greenlee crimping tool is UL listed for range taking on a variety of such devices without regard to how the connector itself is listed.

if nothing else you could do something like what you do to connect a motor up.
 
Thanks for the feedback everyone!

They do make a compression fitting with a Cu reducer adapter to go from 4/0 to #2. We thought about using the terminal plugs but the new equipment has a new disconnect location that is slightly longer than the existing circuit. I suppose I could splice the 4/0 to a 4/0 and then use the terminal plug.
 
There's no problem with your original plan. It's done all the time for voltage drop considerations. As long as a replacement breaker is installed to match the ampacity of the new section, ampacity of the terminations, or the maximum overcurrent protection rating of the new unit. Whichever is less.
 