Splicing Service Cable

Status
Not open for further replies.

gerry

Member
Location
New Jersey
Are there any violations for splicing a service cable that isn't long enough for termination on the neutral bar and main breaker within a residental box or do you have to run new from the meter pan? It seems o.k after reading 110.14b and 300.13 just wanna make sure I'am not missing something.Thanks and have a good day
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Splicing Service Cable

110.14 b allows splicing and as long as you have adequate space in the enclosure you'll be ok. Where will the splice be?
 
Status
Not open for further replies.
Top