Before 1999 NEC you could have splices and taps in a service entrance IF you had 2 or more service switches. Whether or not that was done with 1 meter or multiple meters was a different story. Evnetually, the rules had to be simplified for various reasons.
Part of the reason for easing restrictions on splices is that in some areas underground wiring for a service had to go into a pull box with a slack loop in it so that ground movement would not break off a meter terminal. Another problem arises if an underground service is rather long and needs to be spliced in handholes.
Even for an overhead service there may be wire pulling problems that necessitate a splice.
Also, in some annex B applications the underground wire is larger than what a meter socket or panelboard will accept, even if you can install oversize lugs. For instance, a duct bank off of a padmount transformer could have 6 ducts, 2 for the primary wires ( 1 duct used, 1 spare ) and 4 ducts serving 4 houses. If each house has a 200 amp service the conductors could easily be 500 KCM aluminum. This would have to be spliced in a pull box before each meter. In this size range the best way to terminate an aluminum wire is to use aluminum alloy weldment lugs from
www.sefcor.com that would be welded to the wire using the tungsten inert gas process.