My question is regarding article 400.9 of the 2002 NEC Code and how this may be applied to a temporary power distribution set up at a construction site. I feel that the taps used to provide power the 1hp pumps is in violation of this article. Any comments would be helpful. Here is my description of the site:
20 to 25 well pumps, reported to be 1hp each, were powered by a temporary generator. The primary cable used to provide power to the well pumps consisted of a hard service cord (type SOOW) routed along the surface of the ground along the entire length of the trench where the pumps were located. At each pump location, a secondary cable consisting of a receptacle on one end was tapped onto the primary cable in such a way that the (continuous) primary cable consisted of a series of taps coinciding with the location of each well pump. The receptacle provided at one end of the secondary cable provided a manual disconnect for the cord-and-plug connected pump.
20 to 25 well pumps, reported to be 1hp each, were powered by a temporary generator. The primary cable used to provide power to the well pumps consisted of a hard service cord (type SOOW) routed along the surface of the ground along the entire length of the trench where the pumps were located. At each pump location, a secondary cable consisting of a receptacle on one end was tapped onto the primary cable in such a way that the (continuous) primary cable consisted of a series of taps coinciding with the location of each well pump. The receptacle provided at one end of the secondary cable provided a manual disconnect for the cord-and-plug connected pump.