Splicing the EGC's

Status
Not open for further replies.

JES2727

Senior Member
Location
NJ
When terminating EGC's in a panel and the ground bar does not have enough terminals, is it permissible to splice several ground wires under a wirenut with a pig tail to the ground bar??
 
When terminating EGC's in a panel and the ground bar does not have enough terminals, is it permissible to splice several ground wires under a wirenut with a pig tail to the ground bar??
Sure as long as the pigtail is at least as large as the largest egc in the bunch.
 
Sure as long as the pigtail is at least as large as the largest egc in the bunch.

I did not know this, you learn something new everyday. I guess I figured you would have to upsize the EGC so I never looked into it. I guess it's not likely to have faults on multiple circuits at the exact same time so it wouldn't matter, eh?
 
I did not know this, you learn something new everyday. I guess I figured you would have to upsize the EGC so I never looked into it. I guess it's not likely to have faults on multiple circuits at the exact same time so it wouldn't matter, eh?

Yup kind of similar to pulling one EGC in a raceway with multiple circuits. {250.122(C)} You would just need to size it according to the largest circuit.
 