Re: Splicing the secondary side of a transformer?
The NEC Section 240.21(C) does not permit to tap the secondary conductors of a transformer, expect as permitted by Section 240.21(C)(3), which is for industrial location only.
The NEC does permit to tap a tap as stated in 240.21 Location in Circuit.
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (G). No conductor supplied under the provisions of 240.21(A) through (G) shall supply another conductor under those provisions, except through an overcurrent protective device meeting the requirements of 240.4.