I have an installation where the motor location is class 1 div 2, and the VFD is in a nearby unclassified building. Their is cable tray from the vfd building to the building where the motor is, then the existing cable leaves the tray into a rigid conduit down a wall and goes under the slab for 20 feet before coming out to attach to the motor. The existing cable is just tray cable and not VFD shielded cable, thus the problem. They are getting interference on their Modbus system when the motor is started. I plan to replace the existing VFD, install a line reactor, and replace the tray cable with VFD cable. The problem I have is that the existing conduit from the tray to the motor is only 2", and the cable size needs to be 4/0, which, by the 53% fill is not allowable. Should I install a junction box after the cable leaves the tray and splice onto the existing cable in the conduit? How would I terminate the grounds and the shield at that point, bond to the enclosure and conduit? Removing the slab to install a larger conduit is not and option. Any recommendations?