Hello everyone. I have limited knowledge in residential wiring and i need to know if it is legal to splice romex inside a breaker box. If so are there any specific methods stipulated.
dtshideler said:If so are there any specific methods stipulated.
The solder wasn't holding the splice together either.The old friction tape splices were fine because the wires were first soldered. The tape wasn't holding the connection together it was merely insulating it.
Don110.14(B) Splices Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose.
Do you mean 404.3(B) ...the part where it says:bill@nkapc said:Read 404.3 This may lead you not to use a panelboard as a raceway
So let's go back to 312.8 as directed...(B) Used as a Raceway.
Enclosures shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless the enclosure complies with 312.8.
The "unless adequete space" provision is the rule that allows a splice in a panelboard. So unless you have some ancient FPE panel that is still in use in question, I would think it is very safe to assume you will not reach the 40%/75% limitations in 312.8 with today's panels and a little planning.312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
don_resqcapt19 said:The solder wasn't holding the splice together either.
Don