splicing

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
No.
You would either be paralleling them from one source and violating 310.10(J), or feeding them from two OCP means, a violation of 240.8
 

kimrichi

Member
No.
You would either be paralleling them from one source and violating 310.10(J), or feeding them from two OCP means, a violation of 240.8

so how i service a range with that load where i suppose to subdivide the circuit according to 422-11-B
 