I have a building being rebuilt which has a 400a service (cl320 meter) that I want to split into (2) 200a split services to (2) load centers - these are on the same meter which is what we want.
We definitely want to split the 400a into (2) 200a load centers which are already wired and are located at opposite ends of the building.
There is a 400a service disconnect after the meter which will stay, so everything to be done is after that service disconnect.
The current service is split into (2) 200a services via a 400a Cutler Hammer Genswitch ATS which has 4 lugs, but the generator is trash.
1. Anyone know if the ATS needs to be replaced with age, as it appears to be industrial quality and in fine condition but I don't know what the age or service life of these is?
IF I GET A NEW ATS
2. Most new ATSs only have 2 lugs it seems, even in the 400a lines. Anyone know a 4 lug manufacturer?
Alternately, what equipment should I investigate to split a 400a split phase service into (2) 200a split phases services if I do it after the ATS?
We definitely want to split the 400a into (2) 200a load centers which are already wired and are located at opposite ends of the building.
There is a 400a service disconnect after the meter which will stay, so everything to be done is after that service disconnect.
The current service is split into (2) 200a services via a 400a Cutler Hammer Genswitch ATS which has 4 lugs, but the generator is trash.
1. Anyone know if the ATS needs to be replaced with age, as it appears to be industrial quality and in fine condition but I don't know what the age or service life of these is?
IF I GET A NEW ATS
2. Most new ATSs only have 2 lugs it seems, even in the 400a lines. Anyone know a 4 lug manufacturer?
Alternately, what equipment should I investigate to split a 400a split phase service into (2) 200a split phases services if I do it after the ATS?