When the indoor unit of a split-system A/C unit gets power from the outdoor condensing unit, does the indoor unit require a local disconnect switch if the outdoor unit has a lockable disconnect switch?
Suggest you read thru the rules in 430.102
It doesn't seem to me that the question is specific to ductless systems. I have a ducted system where the air-handler gets its power from the outside condensing unit.Looks like you're talking about a "Ductless" system, which the inside air handler receives its power from the outside condensing unit. ...
That doesn't make a difference to whether 430.102 applies.The Ductless or Mini Splits are all direct current.
It doesn't seem to me that the question is specific to ductless systems. I have a ducted system where the air-handler gets its power from the outside condensing unit.
That doesn't make a difference to whether 430.102 applies.
Can't tell from here. There are quite a few options in 430.109.I only install "Daikin" and the inside fan unit has an on/off button, does that meet NEC 430.102 ?
It doesn't seem to me that the question is specific to ductless systems. I have a ducted system where the air-handler gets its power from the outside condensing unit.
That doesn't make a difference to whether 430.102 applies.
FujitsuMay I ask, what brand and model number are your ducted system, which provide the inside are-handler power from the outside condensing unit ?
Fujitsu
DC or AC doesn't matter for this topic.The only systems I could find that get power from the outside condensing unit are ductless systems which are all dc.
DC or AC doesn't matter for this topic.
I also have a Fujitsu indoor air handler powered only by the outdoor unit. [I installed a double pole snap switch as a disconnect.] It's one of their Slim Duct low static pressure units, similar to this one, although my model number is different:
Slim Duct - AIRSTAGE SINGLE-ROOM MINI-SPLIT SYSTEMS - Residential - FUJITSU GENERAL United States & Canada
Slim Duct - AIRSTAGE SINGLE-ROOM MINI-SPLIT SYSTEMS - Residential - FUJITSU GENERAL United States & Canadawww.fujitsugeneral.com
Cheers, Wayne
How are you saying ducted air handlers are normally powered?The only systems I could find that get power from the outside condensing unit are ductless systems which are all dc. The inside ducted air- handlers are all 220 AC which requires a disconnect. I have never seen an inside ducted air-handler powered from an outside condensing unit.
Agree with your observation. Washington’s AHJs do a good of of understanding the NEC, and adopting reasonable rules where the NEC is not clearFrom my experience, the requirement for a disconnect is not addressed universally in every jurisdiction. As noted, most inspectors apply 430.102 and often do not require a local disconnect per 430.109(B)
IMO this is a motor operated appliance and 422.31 should apply. ...