Split AC unit

Status
Not open for further replies.

Purr24

Member
Location
Pennsylvania
Occupation
Electrician
Can I run the feeder for the outdoor unit in the same conduit with the indoor unit? Outdoor unit feeds the indoor unit. Thanks
 
Can you provide more details about the installation such as residential or commercial, location of the units, wiring methods, mini-split or traditional heat pump / condensing unit with an indoor air handler?
 
Can you provide more details about the installation such as residential or commercial, location of the units, wiring methods, mini-split or traditional heat pump / condensing unit with an indoor air handler?
curious as to why you ask. Under what conditions whould the answer be other than "yes": ?
 
Two reasons, mainly because I am curious and like to have some facts before providing input ;)and the other relates to the variety of questions about the cable used to interconnect the units in mini-split systems.
 
Location doesn't matter, to the OP there is no general restriction, however, you need to consider wire fill, derating, etc,
 
Last edited:
It is a condensing unit on the roof and air handler in data center. Condensing unit is 2#8 &1#10grnd. 40 amps 208v and this feeds the indoor air handler w/ 3-#12thhn.I need to run pipe in a 4 story shaft to the roof and want to run everything in one 1"EMT is this legal?

Sent from my Pixel 2 XL using Tapatalk
 
1. Look at wire fill, 2 #8s, 1 #10, and 3 #12s in a 1" EMT
2. You have 4 CC conductors, need to adjust ampacity for more than 3.
Pretty basic for an electrican, let us know what you come up with and we can check
 
Correct me if I'm wrong been a while.
#8 THHN is rated for 55amps at 90 degrees
4-6 conductors is derate at 80 percent
55 X .80= 44amps
I will install on a 40 amp breaker

Sent from my Pixel 2 XL using Tapatalk
 
It is a condensing unit on the roof and air handler in data center. Condensing unit is 2#8 &1#10grnd. 40 amps 208v and this feeds the indoor air handler w/ 3-#12thhn.I need to run pipe in a 4 story shaft to the roof and want to run everything in one 1"EMT is this legal?

Sent from my Pixel 2 XL using Tapatalk
Where does your 40 amps come from? If MCA then you are likely on right track, if it is MOCP there is a fairly good chance MCA is enough less that you possibly can use 10 AWG. Would need a MCA of no more than 32 if you also have adjustment factor of 80%.

Then comes the air handler conductors. If no heat strips are involved many those only draw 2-3 amps max and would be fine on 14 AWG, even after ampacity adjustments in nearly all cases.
 