Purr24
- Pennsylvania
- Electrician
Can I run the feeder for the outdoor unit in the same conduit with the indoor unit? Outdoor unit feeds the indoor unit. Thanks
curious as to why you ask. Under what conditions whould the answer be other than "yes": ?Can you provide more details about the installation such as residential or commercial, location of the units, wiring methods, mini-split or traditional heat pump / condensing unit with an indoor air handler?
Where does your 40 amps come from? If MCA then you are likely on right track, if it is MOCP there is a fairly good chance MCA is enough less that you possibly can use 10 AWG. Would need a MCA of no more than 32 if you also have adjustment factor of 80%.It is a condensing unit on the roof and air handler in data center. Condensing unit is 2#8 &1#10grnd. 40 amps 208v and this feeds the indoor air handler w/ 3-#12thhn.I need to run pipe in a 4 story shaft to the roof and want to run everything in one 1"EMT is this legal?
Sent from my Pixel 2 XL using Tapatalk