are split bolt connectors listed for out door use? example tying grounding conductors from ground rods to the split bolt should it be taped if it is allowed?
My opinion, for a grounding conductor that doesn't need insulated why tape the connection? Tape will hold more water in the connection and possibly increase corrosion than no tape will.are split bolt connectors listed for out door use? example tying grounding conductors from ground rods to the split bolt should it be taped if it is allowed?
Welcome Doug, There is no harm in going above and beyond code requirements.
wireman1,
We could use a bit more information. Are you looking to connect a ground wire to a ground rod?
A acorn clamp such as Blackburn part number G5 is UL rated for direct burial. This G5 is for 5/8? ground rods to 10 Solid to 2 stranded wire.
Are you asking if split bolts are rated for direct burial? In addition to agreeing with the other post about the ground wire not being interrupted, mechanical connectors labeled with a ?DB? are tested and listed to UL486C, UL467 for grounding and for direct burial. One example of a split bolt that carries this direct burial rating is Blackburn # 2H. I would need exact wire size to give you a selection.
Funny story. Building my own home I used ?? copper ground rods and compression ground grid connectors, crimped using a 15 ton hydraulic head. I still remember the confused look on the inspectors face.
wireman1,
We could use a bit more information. Are you looking to connect a ground wire to a ground rod?
A acorn clamp such as Blackburn part number G5 is UL rated for direct burial. This G5 is for 5/8? ground rods to 10 Solid to 2 stranded wire.
Are you asking if split bolts are rated for direct burial? In addition to agreeing with the other post about the ground wire not being interrupted, mechanical connectors labeled with a ?DB? are tested and listed to UL486C, UL467 for grounding and for direct burial. One example of a split bolt that carries this direct burial rating is Blackburn # 2H. I would need exact wire size to give you a selection.
Funny story. Building my own home I used ?? copper ground rods and compression ground grid connectors, crimped using a 15 ton hydraulic head. I still remember the confused look on the inspectors face.