Hi All,

I have a GE panel circa late 70's (house was built in 78). It's a split bus, with the big loads up top, and then everything else on the lower bus with a 60amp breaker feeding it. I just bought a Chevy Volt, and want to install a Level 2 charger, which is going to want a 40-50amp 240v breaker (which, obviously, is going to mean that 60amp breaker is potentially going to trip if things go right/wrong).

The panel sticker (inside door) indicates the breaker for the lower bus can be a max of 100amps. But I can't tell what gauge the jumpers are from the 60amp breaker to the lower bus (they're covered in scotchlok). Would these have been 4awg copper from the factory (and therefore should handle the 100amps over the 4-6" they are), or would those have been installed by the original installer?

My service is 200amps. Looks like the panel is good to 225amps. Basically, can I just swap out that 60amp breaker for a 100amp, or should I look at swapping out the jumpers as well?

I'm also going to have to do some swapping for normal "thick" breakers to thin breakers...

Thoughts?
 
[FONT=&quot]I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report.gif
button at the top right corner of the post.[/FONT]

[FONT=&quot] [/FONT]
 
Status
Not open for further replies.
Top