That doesn't look like a split bus. Did you take the cover off?
It must be copyrighted and you haven’t paid upfront to view it, like me.Not seeing any picture..
That is probably itIt must be copyrighted and you haven’t paid upfront to view it, like me.
Not seeing any picture..
Not seeing a link, attachment, or anything else besides the text in the OP.Wierd, I can see it but when I click on it to enlarge I get an error message.
Not seeing a link, attachment, or anything else besides the text in the OP.
Is an apparent deleted post that shows up between post 1 and post 2, possible moderators see more information of that one then other users? Comment I can see in that deleted post indicates Little Bill possibly tried to merge an image from that post into the OP? Must have failed though?
I can see and enlarge pics.
I think little bill may be correct, does not look like a split bus to me either.
Now I see pictures from your recent post. Older QO breakers 80-125 amps used to take up 4 spaces in the panel, not 4 adjacent spaces but rather two adjacent spaces along with 2 spaces across from them, but the handle was only on one side - Pretty sure that is exactly what you have there.Whats up the space labeled "main" with no operating handle?
Now I see pictures from your recent post. Older QO breakers 80-125 amps used to take up 4 spaces in the panel, not 4 adjacent spaces but rather two adjacent spaces along with 2 spaces across from them, but the handle was only on one side - Pretty sure that is exactly what you have there.
Both factory installed mains as well as branch breakers rated 80-125 amps were like this at one time. Don't know when they changed to current design which only uses two spaces of the panel - current design has been around at least as long as I have been in the trade which is about 30 years.
It appears you are correct. If you enlarge the pic you will see a label (sticker) that has been added. Someone wrote on it "inside panel) with an arrow pointing to that top right breaker, which is directly across the one labeled "main".
The "main" label isn't a left side of panel breaker, look carefully there is no handle on the left side top two spaces. It is older QO 100 amp breaker that fits full width of panel.
It maybe is possible this is a main lugs only panel and that 100 amp breaker is a feeder breaker for the "inside panel" of the house. That makes all the breakers in this panel a service disconnecting means if that is the case. Don't know if the panel was listed for use as service equipment without a main breaker at that time, today's equivalent QO loadcenter to that one would not be.
You didn’t and one seldom, if ever, pulled the meter even when we were allowed to.The 100 amp breaker feeds a subpanel in the kitchen.
What I didn't understand is how you would kill power to the panel to add a breaker or service it without pulling the meeter.