Have a question on the neural for older split-bus panels. There is an older split-bus panel with one section being normal/emergency and the other being emergency only. The panel is 1-phase 120/240 with each bus 100A rated. The panel currently uses the conduit as ground, separate phase conductors to each bus, but uses a common neutral. The existing panel is going to be reconnected to a generator system with a new E-only and N/E panel. The phase conductors aren't an issue, nor is the ground, but can the single neutral go to a JB then split/tapped so it is connected to both the new E-only and N/E panel? Not sure if the existing split bus panel has separate neutral bars or a single neutral bar.
If this is done, the possibility exists that one new panel can be off and the other on and there could be neutral current going to the panel turned off.