Split bus panel overload protection

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I was at a condo today with a 150 amp split bus panel. During a remodeling project a subpanel was installed next to the main panel. The sub panel is fed by a 70 amp breaker in the upper part of the split bus panel. In addition to the 70 amp there is a 70 amp (heat) 40 amp (range) 40 amp (heat pump) etc.

So, how are the service conductors protected if someone overloads the top part of the panel?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If they are indeed "service" conductors with no Line side protection prior to your panel, they are not protected.
 