I have an existing 100 amp split bus panel in a residence. I need to get additional breaker space and am looking to install a sub panel next to it.
There is currently the “main lighting” 2 pole breaker feeding the lower bus.
In the factory labeled “main disconnect “openings there is a 2 pole breaker for the range and then 2 single pole breakers.
Is it code compliant to remove the 2 single pole breakers and install a 2 pole breaker to feed the new sub panel?
I could then re feed the 2 single pole loads from the new sub and add my new load.
This set up would allow for all power to be disconnected with 3 double pole breakers.
It’s a 100 amp service, total connected load with new circuits would be 77A.
Thank you.
There is currently the “main lighting” 2 pole breaker feeding the lower bus.
In the factory labeled “main disconnect “openings there is a 2 pole breaker for the range and then 2 single pole breakers.
Is it code compliant to remove the 2 single pole breakers and install a 2 pole breaker to feed the new sub panel?
I could then re feed the 2 single pole loads from the new sub and add my new load.
This set up would allow for all power to be disconnected with 3 double pole breakers.
It’s a 100 amp service, total connected load with new circuits would be 77A.
Thank you.