Is a split phase transformer on a pole a Delta transformer?
I misread your question the first time around. Delta and wye are terms for three phase power systems. A single split phase xfmr, like on a pole serving a residential neighborhood, is neither delta or wye, tho some can be wired series or parallel for 120 or 240 output.
"Why do they call single phase single phase. It can be confusing to me because there are two hots and a neutral?"
In single phase, you have, at the minimum, two hot wires, or hot/neutral with one waveform between them. The neutral may or not be present, or needed. Your water heater for example uses 240VAC 1 phase. You have 2 hots connected (and a ground), usually coming from a "split phase" 240V 1 phase service.
In a commercial setting, that water heater may be powered from a 208V 3phase panel. Still two hot wires, just with 208V potential instead of 240V.
Where the neutral is, or if there is even one, is irrelevant to a straight 208/240V 2 wire load.
With a neutral and two hots, now you can have 120/208V (single phase) or 120/240V (split phase).
In a split phase application (240V), the neutral is electrically in the middle of those two 120V potentials. There is 120V from neutral to hot and 240V from hot to hot.
In a single phase application (208V), the neutral is not located between those two points, but in the center of 3 points (wye connection) , one of which is not being used. There is 120V from neutral to any hot, but because the hots are only 120* apart instead of 180* as in split phase, the potential (voltage) from hot to hot is only 208V.
With a high leg 3 phase service, the neutral is located in the middle of two points (typically A and C) like split phase, but not the middle of the triangle like a wye connection. Thus with a high leg you have A and C phase 120V to neutral, and B phase is 208V.
Here's a thread with some pics for clarification/visualization:
http://forums.mikeholt.com/showthread.php?t=133976