wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
For a typical 50 kVA single phase transformer with a 120x240V secondary (two 120V coils that may be used either in series for 240V, or in parallel for 120V), when energized, if I measure the voltage across each 120V coil separately, how close are the voltages go to be? Within 1 V, or 1 mV, or 1 microvolt, or . . . ?
A related question is what the typical impedance for the two 120V secondary coils in series would be. Since if the impedance is say 10 milliohms, and the voltage discrepancy is 10 mV, then I believe that 1A would flow between the two two coils when connected in parallel for 120V output. Which presumably is not desireable.
Thanks,
Wayne
A related question is what the typical impedance for the two 120V secondary coils in series would be. Since if the impedance is say 10 milliohms, and the voltage discrepancy is 10 mV, then I believe that 1A would flow between the two two coils when connected in parallel for 120V output. Which presumably is not desireable.