An expansion coupling will also work.
Customer just called and has (4) 4" sch 40 pvc that need to be connected. One side is waterproofed going through a concrete wall and the other side is buried in a trench. What product or technique do you use to connect two fixed pvc pipes?
I like that idea. Can they be used underground?
Sure, we use expansion fittings all the time for repairs underground.I like that idea. Can they be used underground?
They're used in conduit runs that are long enough to be affected by temperature swings, and across building expansion joints, to prevent breaking or buckling.No, just a regular expansion coupling.
They're used in conduit runs that are long enough to be affected by temperature swings, and across building expansion joints, to prevent breaking or buckling.
They also work as a repair coupling underground where a damaged PVC needs to be repaired after the wire is removed.
I never new it was listed for direct burial use. to each his own.
I wouldn't trust the two O rings to be water tight, especially if I were directly entering a foundation at trench depth.
I never new it was listed for direct burial use. to each his own.
I wouldn't trust the two O rings to be water tight, especially if I were directly entering a foundation at trench depth.
I have never seen an underground PVC conduit that didn’t have water in it.
No one stocks slip couplings or split repair duct, so I wouldn’t hesitate to use an expansion coupling underground for a repair.
And for those that say that you would never use a product in conflict with its listing, you are full of it.
There are even people that think an expansion coupling is required underground on long runs the same as above ground.
I never new it was listed for direct burial use. to each his own.
I wouldn't trust the two O rings to be water tight, especially if I were directly entering a foundation at trench depth.
Conduit is not pressure rated, it is not intended to be water tight.
If you were concerned about directly entering a foundation and the possibility of water intrusion, an expansion fitting installed in the run should be the least of your concerns.
You should already have another method to mitigate water. Such as a drain hole, slope the run the other direction, polywater foam sealant, etc.
Well I guess you have never run across any of my underground conduit runs.![]()
I didn't say never I said I don't trust it.
Just because something is listed for an application that doesn't mean it the best product for the job. example the PVC two hole conduit straps hold up like crap when used out doors especially where exposed to direct sun light.
Like I said to each his own.