The NEC does not require the use of a two pole breaker for this application. It only requires a means to simultaneously disconnect the ungrounded conductors. Approved handle ties on single pole breakers meet this requirement.what you would need for a split wired receptacle would be a 2 pole breaker,
Will what?Originally posted by hurk27:
The 2005 will.
That does not meet the code rule. The means to simultaneously disconnect the ungrounded conductors must be provided at the branch circuit panel.put the breakers in one on top of the other,use your index and middle finger of one hand and you can shut them both off simotaneously,beats any handle tye ever made.