Is there any 2011 NEC requirement stating that the top half of a split wired receptacle be hot all the time while the bottom half of the split wired receptacle be switch controlled?
2-189 Log #1409 NEC-P02 Final Action: Accept in Principle
(210.52)
____________________________________________________________
Submitter: George Stolz, II, Pierce, CO
Recommendation: Add the following to 210.52:
Receptacles in the areas defined in this section shall be permitted to be
switched, provided uninterrupted receptacles are installed at the spacings
required by this section.
Substantiation: As this section is currently written, there is no prohibition
from allowing the required receptacles to be switched. A requirement that
constant power is required at the intervals specified in 210.52(A)(1), and (C)(1)
would add clarity to the existing text. It is generally perceived that this section
is to reduce the use of extension cords in residences. The prohibition of
switching required receptacles would further assure this reduction.
Panel Meeting Action: Accept in Principle
Panel Statement: The recommended action is accomplished through the panel
action on Proposal 2-190.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 11 Negative: 1
Explanation of Negative:
BROWN, L.: Please see NAHB?s Ballot Comment on Proposal 2-190.
____________________________________________________________
Is there any 2011 NEC requirement stating that the top half of a split wired receptacle be hot all the time while the bottom half of the split wired receptacle be switch controlled?
If the receptacle is installed to count as one required by the 6'/12' rule then yes one half must be unswitched. I believe that George wrote that code change.
I agree with Trevor. If you switch the entire receptacle that is fine but then you must add another one to satisfy the placement required in 210.52
I might be wrong but it sounds like the OP was asking if the code stated which half of the receptacle had to be switched.
I might be wrong but it sounds like the OP was asking if the code stated which half of the receptacle had to be switched.
Or, if switched, whether the top or bottom is required to be.
I was aware of how splitting a receptacle might affect the code requirements for spacing (i.e. 6'/12').
My question revolved around a discussion with another electrician who said that when splitting
a duplex receptacle, the top half had to be hot all the time, while the bottom portion had to be switched.
I was aware of how splitting a receptacle might affect the code requirements for spacing (i.e. 6'/12').
My question revolved around a discussion with another electrician who said that when splitting
a duplex receptacle, the top half had to be hot all the time, while the bottom portion had to be switched.
.......... 480 and I have the same mind set. SCAREY!