Hello, first post. I’m looking for options / opinions to feed 2 sub panels from new meter main (outside wall of detached garage). My current plan is to split (Polaris) the 200 amp feed from the meter main right before the sub panel inside the garage.
Both panels will be 200 amp main breaker panels, the new meter main is 200 amp Solar ready 12 space and 2 of the spaces will have plug on feed thru lugs that power the sub panels and are protected by the 200 meter main breaker.
Some background: The current setup has a power pole on the side of the property with a 10k transformer that serves 2 homes. The drop comes in front of the detached garage, across a patio (about 10 ft off the ground) and to a weatherhead near the back of the main level of the house. Meter socket on the siding (no disconnect) then into the house with a 35 year old GTE 200 amp main panel right behind the meter which feeds a 50 amp sub panel in the garage and a 100 amp sub panel in a mechanical room at the front of the house.
The power company is in the process of upgrading the transformer (25k), and I am planning on undergrounding the service (about 50ft) from the pole to the side of the garage (new meter main). From there I will install SER up and over from the right side of the garage to the left, splice the SER with one set of wires going to the new garage panel (also current location of the existing garage panel) the other set will switch to individual conductors to go into conduit under the patio deck and to an 200 amp outdoor panel (same location as existing meter socket. From there I will use the existing 200 main location to extend all the circuits and sub panel feed as needed keeping all the junctions accessible.
Leviton Solar ready Meter main
Leviton outdoor main breaker panel
Leviton indoor main breaker panel
All plug on neutral panels
No option with these panels fir a bolt on Feed through lug (as far as I know)
Both panels will be 200 amp main breaker panels, the new meter main is 200 amp Solar ready 12 space and 2 of the spaces will have plug on feed thru lugs that power the sub panels and are protected by the 200 meter main breaker.
Some background: The current setup has a power pole on the side of the property with a 10k transformer that serves 2 homes. The drop comes in front of the detached garage, across a patio (about 10 ft off the ground) and to a weatherhead near the back of the main level of the house. Meter socket on the siding (no disconnect) then into the house with a 35 year old GTE 200 amp main panel right behind the meter which feeds a 50 amp sub panel in the garage and a 100 amp sub panel in a mechanical room at the front of the house.
The power company is in the process of upgrading the transformer (25k), and I am planning on undergrounding the service (about 50ft) from the pole to the side of the garage (new meter main). From there I will install SER up and over from the right side of the garage to the left, splice the SER with one set of wires going to the new garage panel (also current location of the existing garage panel) the other set will switch to individual conductors to go into conduit under the patio deck and to an 200 amp outdoor panel (same location as existing meter socket. From there I will use the existing 200 main location to extend all the circuits and sub panel feed as needed keeping all the junctions accessible.
Leviton Solar ready Meter main
Leviton outdoor main breaker panel
Leviton indoor main breaker panel
All plug on neutral panels
No option with these panels fir a bolt on Feed through lug (as far as I know)