I guess I should clarify my point in posting the pictures - How would you do it?
My temp is crossing the road, and the driveway. This was the most reasonable way to get the job done, as far as I could think of.
(I'm not real proud to admit it, but in the past I have done similar, sans the sealtite and junction box - just had the URD popping out the top of the riser, taped back over to the riser and spliced to a temp - which this is an improved version of.
Jim Walker said:
does that stand pass 110.26 ?
Probably not - but these are used in my area every day without much of a thought to it. It hadn't occurred to me until you brought it up.
As far as neatness i would not care on a temp.
You cared three posts prior.
Does this stand qualify as a structure and need ground rods ?
Yes, and I installed a ground rod at the temp. I also did not pull an EGC, as Colorado has decided that if a service disconnect cannot serve more than one feeder, then that feeder can omit the EGC (contrary to the change in the 2008.)
So, how would you (general "you", not just Jim) tackle the problem?