Spot the violation(s)

Status
Not open for further replies.

220/221

Senior Member
Location
AZ
As usual, I am fixing other peoples crap. Someone did a service upgrade/relocate in the 80's..obviously bootlegged. The used the old panel box for a JB.

Bad pics...wrong camera setting on the before pics.

This is the panel I asked about last week. It is directly over a gas meter. When they relocated the service the ran 1 1/4 emt and back fed 7 120V circuits, the 240V 50 amp A/C and a 240V 30 amp dryer.

Feed from right, A/C circuit out the left.


DSC01547.jpg


The neutrals were split bolted 6 to a single #8.

DSC01546.jpg


I changed to a real JB, pulled the back fed circuits out ( except A/C) and installed a 60 amp sub to the left. I put in GFCI breakers to protect the old 2 wire system. Maybe instead, I should have put in a 60 amp GFCI main but it JUST occured to me.

DSC01550.jpg


DSC01551.jpg


There are still some violations but this will pass. Count them up.:grin:


PS. There IS a plastic snap in bushing in the back of the JB (Peter). It just didn't show up to well in the pic. There is one in the panel also for the 3 new circuits.
 
Last edited:
Read my edit :wink:

It actually WAS an old school blue one. The new black ones are more photogenic.
 
Looks are just that!

Looks are just that!

Thats a full 2'-0" of conduit!
I thought the biggest ground wire in the can had to be the bounding ground!
 
Your branch circuit conductors appear to be undersized

??? Derating????

#12 conductors. 3, 15 amp circuits and 4, 20's.

Existing AC from service panel is 50 amp #6 thhn to SE.


I thought the biggest ground wire in the can had to be the bounding ground!

There is only one ground in there....a #10.
Wrong???
 
220/221 said:
??? Derating????

I am not saying it's going to melt down but how many current carrying conductors do you have in there?

Anything over 9 will kill you on the 15 and 20s and that larger one really will take a hit.
 
stickboy1375 said:
Yes, but apparently in AZ they just don't give a crap... :roll: :wink:
Functionally, I'm not sure what the big deal is, really. Sure, it's a violation, but what's it hurting? You can fish cables into or out of a single gang Carlon new work box during an old work situation, and they don't have connectors. I smell a proposal. It wouldn't get approved, I feel sure, but a worthy proposal just the same.
 
mdshunk said:
Functionally, I'm not sure what the big deal is, really. Sure, it's a violation, but what's it hurting?

I agree, this is not the kind of violation that creates a real fire or shock hazard.
 
I am not saying it's going to melt down but how many current carrying conductors do you have in there?

Depends on how you define "CCC". The last time it came up, the city inspector who seemed knowledgable, said neutrals didn't count.;) I would define neutrals as CCC's but I'm going with what he said. That makes 9 :cool:

Violations:

more than 9 CCC's.
paint not scraped off under the lug.
blue wing nuts on #6 wire.
emt fittings not the new rain tite style.
no connectors in JB/panel
self tapping screw into bond jumper in panel.

It looks a heck of a lot better though :wink:
 
Good Job

Good Job

220/221 said:
It looks a heck of a lot better though :wink:

I know countless inspectors who let the nit picky, so called gray areas slide because it's a clean, proffesional install, and better than when you found it, based on an understanding of what's practical and safe in real world application.

It's better, safer, and closer to the intent and purpose of the code.
Advancement......Progress. Nit picking aside, Progress.

What's that saying....Rome wasn't buit in a day....or something.


Debate away. :smile:
 
220/221 said:
Depends on how you define "CCC". The last time it came up, the city inspector who seemed knowledgable, said neutrals didn't count.;) I would define neutrals as CCC's but I'm going with what he said. That makes 9 :cool:

'Real' neutrals do not count. Like the neutral in a multwire branch circuit, or the neutral in a feeder. They are not current carrying conductors.

The white wire of a two wire circuit is not a neutral, it is a grounded conductor and it is a current carrying conductor.

I would have run two or three smaller raceways to avoid the deratiing.
 