LARRY POTTER
Member
in spray boothes where mineral spirit based material is applied do the emergency stops have to be class 1 div 1 for eplosion proof as well as the conduit having to be rigid threaded conduit
What are the emergency stops for? The booth interior is Class I, Division 1. Areas immediately outside booth openings are Class I, Division2.
See article 516 to determine the classified areas. For more info, see NFPA 33 Standard For Spray Application Using Flammable or Combustible Materials.
Depending on what you are "stopping" it may be easier to use pneumatics. Or use a pneumatic pilot to operate a remote electrical switch that can be located outside of the classified arera. Either would be less expensive to install and much easier to maintain.