is sprinkler piping and heads allowed in the dedicated space above panelboards if a drain pan is installed
The "dedicated space" indicated at 110.26(F)(1)(a) is the space equal to the depth and width of the equipment, not the room space. So if you took a plumb bob from the floor to the structural ceiling at the corners of the equipment this would designate the actual dedicated space. The sprinklers could be located outside of this space.
View attachment 2459
Agreed....Don't get the Dedicated Equipment Space Requirements confused with the Dedicated Working Space requirements. Read 110.26 fully.