sprinkler in dedicated space

Status
Not open for further replies.
nec handbook

nec handbook

the handbook says sprinkler protection is allowed if it complies with 110.26(F)
(1)(d). this refers to dropped ceilings. exhibit 110.19 shows sprinkler piping not entering the dedicated or working space but that it is afforded either space. does this mean sprinkler piping can be in either space as long as it serves this space and does not just pass thru the area? am i reading this right that sprinkler protection is the only thing that can penetrate the dedicated space and that no drain pan would be required? thanks
 
The "dedicated space" indicated at 110.26(F)(1)(a) is the space equal to the depth and width of the equipment, not the room space. So if you took a plumb bob from the floor to the structural ceiling at the corners of the equipment this would designate the actual dedicated space. The sprinklers could be located outside of this space.
View attachment 2459
 
The "dedicated space" indicated at 110.26(F)(1)(a) is the space equal to the depth and width of the equipment, not the room space. So if you took a plumb bob from the floor to the structural ceiling at the corners of the equipment this would designate the actual dedicated space. The sprinklers could be located outside of this space.
View attachment 2459


Or

6 feet above the equipment, whichever is closer. :wink:
 
Don't let anything in our dedicated space. Who care's who it inconvience. Make'em move anything that is in you dedicated space. :D
 