Hi,
while performing a general inspection in a new housing project i found that each house has a dedicated telecom room, the room has a telecom rack and a dedicated telecom grounding busbar, and since there is no dedicated electrical room in the house the power system main busbar is located in the telecom room, which seems okay please correct me if i am wrong. there is also a light fixture, switch, cable trucking, junction and pull boxes in the room.
My concern is there is a fire protection water sprinkler installed in the telecom room, is this permitted?
i found the following code reference online:
NFPA 13 Clause No. 8.15.11.2 Sprinklers shall not be required in electrical equipment rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure including protection for penetrations.
(4) No combustible storage is permitted to be stored in the
room.''
i am not sure if the walls and door of the telecom room are fire rated, i need to check. and since the power grounding busbar is inside the room, is the room still considered as a telecom room only ?
please advise
while performing a general inspection in a new housing project i found that each house has a dedicated telecom room, the room has a telecom rack and a dedicated telecom grounding busbar, and since there is no dedicated electrical room in the house the power system main busbar is located in the telecom room, which seems okay please correct me if i am wrong. there is also a light fixture, switch, cable trucking, junction and pull boxes in the room.
My concern is there is a fire protection water sprinkler installed in the telecom room, is this permitted?
i found the following code reference online:
NFPA 13 Clause No. 8.15.11.2 Sprinklers shall not be required in electrical equipment rooms where all of the following conditions are met:
(1) The room is dedicated to electrical equipment only.
(2) Only dry-type electrical equipment is used.
(3) Equipment is installed in a 2-hour fire-rated enclosure including protection for penetrations.
(4) No combustible storage is permitted to be stored in the
room.''
i am not sure if the walls and door of the telecom room are fire rated, i need to check. and since the power grounding busbar is inside the room, is the room still considered as a telecom room only ?
please advise