Sprinkler pipe above elec. panels
anbm
TX
Designer
I went to job site this morning and saw sprinkler pipe hang at 4 feet above electrical panel, one of the folks said code allow to have that installation as long as the pipe serve electrical room. That is not what I recalled from code requirement (the pipe either need to be 6 ft above panel or have drip pan protection for leak). Do you agree?
I agree with you 110.26(F)
Is not permitted in the footprint of the electrical equipment within 6ft on the top. If above 6ft, then it is permitted if protection is provided to protect the equipment. This covers only the DEDICATED EQUIPMENT SPACE (FOOTPRINT OF EQUIPMENT) not the entire equipment room 110.26 (F) (1) a,b,and c
It's required to be both.
(1) Indoor. Indoor installations shall comply with
110.26(F)(1)(a) through (F)(1)(d).
(a) Dedicated Electrical Space. The space equal to the
width and depth of the equipment and extending from the
floor to a height of 1.8 m (6 ft) above the equipment or to
the structural ceiling, whichever is lower, shall be dedicated
to the electrical installation. No piping, ducts, leak protection
apparatus, or other equipment foreign.
(b) Foreign Systems. The area above the dedicated
space required by 110.26(F)(1)(a) shall be permitted to contain
foreign systems, provided protection is installed to
avoid damage to the electrical equipment from condensation,
leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be
permitted for the dedicated space where the piping complies
with this section.
The sprinkler piping is permitted in dedicated space but need to comlies with this section, this is very conflict, sounds like if we install sprinkler piping in dedicated space we have to protect it. This sounds conflict with freign system piping. (-:
with this section.
with this section.
The Red Highlight says that pipe must be at least 6' above, if it is protected from damaging electrical equipment.
The Blue Highlight says sprinkler protection can be provided for the space if the piping complies with the previous requirements, ie. above dedicated space and protected. No Conflict.
with this section.
Does this mean sprinkler pipe can be inside dedicated space (if protected) not above??? (-:
with this section.
No, this does not allow the sprinkler pipe to be within the dedicated space just that the spray pattern for the sprinkler protection may include the dedicated space. The sprinkler piping can be above the dedicated space, just not in the dedicated space.
Chris