Sprinkler Test Question

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
I must apologize in advance for the horrible way I am about to pose this question: May it torture you as it did me.

My friend just took (and passed) his master's exam, at the tender age of 24. :shock:

He secreted out one question in his head, to put to me, as he couldn't find the answer. Neither could I. My conclusion is that he's remembering the question incorrectly, as it makes absolutely no sense to me. But he claims he spent the remaining time of his test studying the question and trying in vain to find the answer, so the question should be well-recorded in his memory.

Q: A center-pivot sprinkler head has a ground ring (perhaps integral to the head?). What size grounding conductor must be connected to this ring?

A.) Sized according to 80% of the FLC of the motor
B.) Sized according to 90%...
C.) ...100%...
D.) ...125%...
Does this in any way sound remotely familiar to anyone?

1. The idea of jumping to a GEC size from a percentage of an FLC rating of a motor just does not make any sense to me. He said no motor spec's were given in the question, and no conductor sizes were given in the answers.

2. The idea of jumping to a EGC size (if the "ground ring" is an internal component of the sprinkler device) from a FLC doesn't jive with 250.122 either.

Any ideas?
 

jtester

Senior Member
Location
Las Cruces N.M.
If you are referring to a jumper to a rotating ring, then 675.11 applies. It requires the ground to be sized at 125% of the flc of the largest device + the sum of the others. It is possible that 125% is the answer.

Jim T
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
I agree with Don - 100%. Please note that 675.11 is talking about the rating of the ground ring (a component of the irrigation device). It is not talking about the conductor attached to the ring.
 

jtester

Senior Member
Location
Las Cruces N.M.
Please note that 675.11 is talking about the rating of the ground ring (a component of the irrigation device).

Good call, I stand corrected on my code reference. I'm not sure that 125% is incorrect though. 675.13 says 100% of the supply conductor size, but the question is based on percentage of flc. Would the supply conductor be sized at 100% of flc or 125%?

Jim T
 

unimo

Member
Location
Colorado
I would say 125%. I bet if you saw the question it is worded like 675.22 (A), and they're simplifying it by omitting remaining motors.
It does refer specifically to "center pivot" also. usually in those tests, the question has specific wording that matches a certain part of the code book.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
8) 8) You guys are the bomb!!! 8) 8)

I had no idea this article even existed!!!

It's gotta be 675.11(A). That's almost word for word what the question sounded like. Nate's gonna flip. :D

I could have swore I looked up "Irrigation" in the index, I guess I didn't!

Thanks so much Don, Jim, Charlie, and all. 8)
 

unimo

Member
Location
Colorado
Yes that exact question was on my master's test, worded like 675.11 (A),
so it would be 125%. It didn't say center pivot on my test.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
I just called him to tell him, he said he already knew. We had another guy find it on his R.W.

Looks like I need to be looking closer at the back half of the book! ;)

What part of the state you from, Unimo?
 