Anybody have their handy dandy SQ D catalog close by? I need the resistance of a 8536SE01SY59 coil. 120V coil for a size 3 starter.
Anybody have their handy dandy SQ D catalog close by? I need the resistance of a 8536SE01SY59 coil. 120V coil for a size 3 starter.
Do they have resistance published someplace? I'm not finding it. I even did google search for cat number you gave and all that turned up is this thread on this site.
Not sure if they do. Help was at a dairy with starter that would not pull in. Hummed. He had already replaced the control transformer. I suspect replacement was to small.
Or coil shorted. He had about 8 ohms.
Not sure if they do. Help was at a dairy with starter that would not pull in. Hummed. He had already replaced the control transformer. I suspect replacement was to small.
Or coil shorted. He had about 8 ohms.
If it was humming and he had 120v on the coil terminals, I'd say the coil is bad. If the control transformer was bad or weak, I wouldn't think he'd have a full 120v on the coil terminals while it was trying to pull in.
In my opinion the best thing to do is to get the VA for that coil which should be published and assure that your CPT is large enough to provide the VA that is required. It is not often that a manufacturer publishes coil resistance as that value often time is not relevant. If you were to have two starters with the same coils you may try comparing their resistance which may provide some direction.
But first go to the Square D catalog which should have the power requirements listed for the coils of their starters.
He did measure the working voltage at 68 v. Old xfmr was a .1kva. He tried using a .05. Largest we had on hand and was suprised we had that.
Working meaning while the coil was energized.
The thing with the coil is it takes more VA to pull it in than it takes to hold it in.
According to Square D catalog a size 3, 3 pole contactor coil like in the OP requires 678 in-rush VA, and 47 sealed VA.
A transformer would not have to be 678 VA to run this coil, it would just need to be able to deliver that for a short time to pull it in and then only need to provide 47 VA continuously after that.
According to the partial Sola pdf I can access via Google and the info Kwired provided, I need a control transformer capable of 725 va. Good, now if I could just see the rest of that PDF...
According to the partial Sola pdf I can access via Google and the info Kwired provided, I need a control transformer capable of 725 va. Good, now if I could just see the rest of that PDF...
I agree with that and I think your point:That is a big transformer for one coil, it is a somewhat large coil but still doesn't require much power other than at inrush. I think the 150 VA that others have suggested is probably what was needed.
is pretty much spot on.My experience if you have continuity and no melted plastic in the case they are usually good.
If you had ordered a size 3 starter with transformer from Square D, they would have used a 150VA machine tool transformer, their number 9070T150D1.
The transformer we, my help, took out was a ...100D1. IDK if the inrush capabilities are comparable with that of a SOLA 100va, but the Sola would be about 70% of what their sizing rules would suggest. The 50va we had on hand about 30%. We are taking up a 150.