SQ D coil resistance

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
Anybody have their handy dandy SQ D catalog close by? I need the resistance of a 8536SE01SY59 coil. 120V coil for a size 3 starter.

Do they have resistance published someplace? I'm not finding it. I even did google search for cat number you gave and all that turned up is this thread on this site.
 

kwired

Electron manager
Location
NE Nebraska
Not sure if they do. Help was at a dairy with starter that would not pull in. Hummed. He had already replaced the control transformer. I suspect replacement was to small.
Or coil shorted. He had about 8 ohms.

Transformer may have been too small for pull in but if you physically push it in it probably would be large enough to hold it in. Would give you idea right then that the coil was good.

Don't ask me how to physically push it in and comply with 70E though.

My experience if you have continuity and no melted plastic in the case they are usually good.
 
Last edited:

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Not sure if they do. Help was at a dairy with starter that would not pull in. Hummed. He had already replaced the control transformer. I suspect replacement was to small.
Or coil shorted. He had about 8 ohms.

If it was humming and he had 120v on the coil terminals, I'd say the coil is bad. If the control transformer was bad or weak, I wouldn't think he'd have a full 120v on the coil terminals while it was trying to pull in.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
If it was humming and he had 120v on the coil terminals, I'd say the coil is bad. If the control transformer was bad or weak, I wouldn't think he'd have a full 120v on the coil terminals while it was trying to pull in.

He did measure the working voltage at 68 v. Old xfmr was a .1kva. He tried using a .05. Largest we had on hand and was suprised we had that.

Working meaning while the coil was energized.
 
Last edited:

templdl

Senior Member
Location
Wisconsin
In my opinion the best thing to do is to get the VA for that coil which should be published and assure that your CPT is large enough to provide the VA that is required. It is not often that a manufacturer publishes coil resistance as that value often time is not relevant. If you were to have two starters with the same coils you may try comparing their resistance which may provide some direction.
But first go to the Square D catalog which should have the power requirements listed for the coils of their starters.
 

kwired

Electron manager
Location
NE Nebraska
In my opinion the best thing to do is to get the VA for that coil which should be published and assure that your CPT is large enough to provide the VA that is required. It is not often that a manufacturer publishes coil resistance as that value often time is not relevant. If you were to have two starters with the same coils you may try comparing their resistance which may provide some direction.
But first go to the Square D catalog which should have the power requirements listed for the coils of their starters.

The thing with the coil is it takes more VA to pull it in than it takes to hold it in.

According to Square D catalog a size 3, 3 pole contactor coil like in the OP requires 678 in-rush VA, and 47 sealed VA.

A transformer would not have to be 678 VA to run this coil, it would just need to be able to deliver that for a short time to pull it in and then only need to provide 47 VA continuously after that.
 

templdl

Senior Member
Location
Wisconsin
You are correct Kwired.
But it does no good to use a CPT that doesn't have enough VA to even pull in the coil. CPTs are designed diffent than the common transformer in that they do not have an even turns ratio. The becomes evident when you attempt to use one as a step up transformer and find that the HV side puts out a lower voltage than is anticipated. CPTs are designed to help reduce voltage drop while providing inrush current. In other words a 480-120 CPT is not actually a 4:1 ratio but the secondary is slightly higher than 1 which translates to a slightly higher secondary voltage than 120v.
But you still must size the CPT so that it is capable of supplying inrush current even though it is not sized to provide the inrush KVA continually.
When trying to draw too much inrush current from a CPT that is sized too small you will end up with the voltage taking a big nose dive at that time.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
He did measure the working voltage at 68 v. Old xfmr was a .1kva. He tried using a .05. Largest we had on hand and was suprised we had that.

Working meaning while the coil was energized.

That alone tells me it's too small, if the coil was shorted it'd wipe out the transformer secondary fuse.

The thing with the coil is it takes more VA to pull it in than it takes to hold it in.

According to Square D catalog a size 3, 3 pole contactor coil like in the OP requires 678 in-rush VA, and 47 sealed VA.

A transformer would not have to be 678 VA to run this coil, it would just need to be able to deliver that for a short time to pull it in and then only need to provide 47 VA continuously after that.

According to the partial Sola pdf I can access via Google and the info Kwired provided, I need a control transformer capable of 725 va. Good, now if I could just see the rest of that PDF...

FactoryMation has a neat little table in their catalogs transformer section for sizing control transformers. Using the info Kwired provided, it looks like a 150VA transformer is about right. 100VA seems borderline.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
If you had ordered a size 3 starter with transformer from Square D, they would have used a 150VA machine tool transformer, their number 9070T150D1.
 

kwired

Electron manager
Location
NE Nebraska
According to the partial Sola pdf I can access via Google and the info Kwired provided, I need a control transformer capable of 725 va. Good, now if I could just see the rest of that PDF...

That is a big transformer for one coil, it is a somewhat large coil but still doesn't require much power other than at inrush. I think the 150 VA that others have suggested is probably what was needed.
 

Besoeker

Senior Member
Location
UK
That is a big transformer for one coil, it is a somewhat large coil but still doesn't require much power other than at inrush. I think the 150 VA that others have suggested is probably what was needed.
I agree with that and I think your point:
My experience if you have continuity and no melted plastic in the case they are usually good.
is pretty much spot on.

A couple of other points/thoughts.
You can usually tell a burnt out coil by the acrid smell. Once experienced, never forgotten.
If the control panel transformer isn't man enough for the job and the contactor sits there with the coil energised, even at reduced voltage, but not pulled in that will give both the coil and the transformer a very hard time. If it persists for any significant duration, I would expect both to fail. And it to be very obvious that they had.

Just my two cents worth. Or two pence worth...
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Details, details, details

Details, details, details

If you had ordered a size 3 starter with transformer from Square D, they would have used a 150VA machine tool transformer, their number 9070T150D1.

The transformer we, my help, took out was a ...100D1. IDK if the inrush capabilities are comparable with that of a SOLA 100va, but the Sola would be about 70% of what their sizing rules would suggest. The 50va we had on hand about 30%. We are taking up a 150.

The existing 100 had a 10amp fuse on the secondary side. Maybe why the primary side windings went TU. You suppose.

The secondary fuse on the 50 should have blown but, :rant: and there will be a disussion on this, he just used the 10 amp from the original CT.

SQ D just notified me the ohm reading should be in the "single digits" for that coil.

Thank you.

The 8536... # was the starter, not the coil. My mistake. He gave me both.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The transformer we, my help, took out was a ...100D1. IDK if the inrush capabilities are comparable with that of a SOLA 100va, but the Sola would be about 70% of what their sizing rules would suggest. The 50va we had on hand about 30%. We are taking up a 150.

For the most part the characteristics are similar between manufacturers for similar products. A machine tool transformer is designed to provide about 6x inrush, whereas a normal power transformer is only about 4x and a 'furnace transformer' maybe only 3-4x.
 