I want an EPO system to bring down a 200A Square-D QO panel.
The obvious way to do that is with shunt trip breaker.
Does SQD (or should I say al-la Prince "The company until recently known as SQD..."} make a shunt trip breaker in that form factor?
Backstory:
As related before, 600A service with coordination for three adjacent 200 SQD QO panels, and {soon to be} two 200A single-breaker disconnects; each feeding 200A panels elsewhere. The new panel feeds the swimspa, sliding floor, three 2HP Pumps, and other stuph. For it we seek EPO functionality.
To me, EPO means a shunt trip breaker. We want to stay with the same SQD panelboard as the other 6-7 on the property. But the EC says there's no such critter as a SQD QO 200A shunt trip breaker. Failing that, ~50 ft away there will be a single circuit 3R breaker/disconnect to feed the panel. Does someone make such a disconnect with a shunt trip breaker option? A third approach?
The obvious way to do that is with shunt trip breaker.
Does SQD (or should I say al-la Prince "The company until recently known as SQD..."} make a shunt trip breaker in that form factor?
Backstory:
As related before, 600A service with coordination for three adjacent 200 SQD QO panels, and {soon to be} two 200A single-breaker disconnects; each feeding 200A panels elsewhere. The new panel feeds the swimspa, sliding floor, three 2HP Pumps, and other stuph. For it we seek EPO functionality.
To me, EPO means a shunt trip breaker. We want to stay with the same SQD panelboard as the other 6-7 on the property. But the EC says there's no such critter as a SQD QO 200A shunt trip breaker. Failing that, ~50 ft away there will be a single circuit 3R breaker/disconnect to feed the panel. Does someone make such a disconnect with a shunt trip breaker option? A third approach?