SqD I-Line Meter CT connections

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
Is anyone familiar with this PM5563 power meter and Smart Cell surge protector combination? I have a customer where the CTs secondary leads look to have their polarity reversed and need to correct it. It was installed by a different electrical contractor, and I am configuring the meter and integrating it with their BAS. I It is not clear to me if I can remove the meter or a cover on the unit while the SPD is installed into the panelboard bus, to get access to the CT lead terminals. There are 800A:5A CT's installed in the i-line and the orientation of those on the service conductors looks correct, and I cannot get to them to flip the CT orientation either. Getting negative power readings on this thing and I think the CT lead polarity is reversed. Do I need to remove the whole unit?