SqD SEF Circuit Breaker

Status
Not open for further replies.

zog

Senior Member
Location
Charlotte, NC
Rack the breaker out to the disconnect position and apply a padlock to the racking mech access cover. Just like any other drawout type breaker.
 

zog

Senior Member
Location
Charlotte, NC
Bolt in, yep you are going to have problems there. Still even thier accessory only stops the breaker from closing, it is not sufficient protection from switching transients, thats why draw out breakers are locked in the disconnect postion. But I suppose it is the best you can do.
 