I am troubleshooting a new, permitted, complete rewire job that includes a new 200 amp Square D Home panel as of 2016 and has been in service with no problems until recently. Really clean install.
Nearly all breakers are dual function AFCI and the others are dumb. Each leg has 123.5 VAC.
Breaker 9 is a DF-AFCI breaker supplies a home office and is frequently tripping but only when a high load appliance on another branch is starting, furnace, microwave, chop saw etc. The lights dim down, brownout of sorts, and then breaker 9 trips. Sometimes other breakers, on the opposite bus, will trip too, like the smoke detector circuit. Although now fixed, the furnace blew its 24vac transformer. At one point we had no appliances plugged in, including power strips, except the LED ceiling light was on and breaker 9 still tripped when the cop saw was started. The ceiling light passed my inspection.
I am stuck! I like to figure stuff out on my own and its hard for me to ask for help but can only beat my head against the wall for so long. I have been through nearly every outlet looking for a loose wire. All neutrals are in twisted pigtails and secured on the outlets.
Is this an internal or external problem and additional insights could you provide? (note: Square D has a quick test procedure that I followed and some tip immediately and others do not. The test tripping appears to pick its circuits randomly.)
Thanks
Nearly all breakers are dual function AFCI and the others are dumb. Each leg has 123.5 VAC.
Breaker 9 is a DF-AFCI breaker supplies a home office and is frequently tripping but only when a high load appliance on another branch is starting, furnace, microwave, chop saw etc. The lights dim down, brownout of sorts, and then breaker 9 trips. Sometimes other breakers, on the opposite bus, will trip too, like the smoke detector circuit. Although now fixed, the furnace blew its 24vac transformer. At one point we had no appliances plugged in, including power strips, except the LED ceiling light was on and breaker 9 still tripped when the cop saw was started. The ceiling light passed my inspection.
I am stuck! I like to figure stuff out on my own and its hard for me to ask for help but can only beat my head against the wall for so long. I have been through nearly every outlet looking for a loose wire. All neutrals are in twisted pigtails and secured on the outlets.
Is this an internal or external problem and additional insights could you provide? (note: Square D has a quick test procedure that I followed and some tip immediately and others do not. The test tripping appears to pick its circuits randomly.)