:-?Hello all,
I took a look at the Square D overload chart and went cross eyed.
I have a 3/4 HP motor. Name plate 1.6 A at 440 V, 3 phase. Standard squirrel cage with internal thermal protection. The existing heaters are tripping 1 hour into operation of a room heater. The controller is mounted about 4 feet to the left at same level. The overload heater size is B2.65, square D contactor size 0. Oh, the service factor on nameplate is 1.0. Do I calculate at 170% due to internal thermal protection? Or should I calculate at 115% service factor? Does anyone have access to info. that could explain how to read the square D heater chart? I would appreciate any assistance.
I took a look at the Square D overload chart and went cross eyed.
I have a 3/4 HP motor. Name plate 1.6 A at 440 V, 3 phase. Standard squirrel cage with internal thermal protection. The existing heaters are tripping 1 hour into operation of a room heater. The controller is mounted about 4 feet to the left at same level. The overload heater size is B2.65, square D contactor size 0. Oh, the service factor on nameplate is 1.0. Do I calculate at 170% due to internal thermal protection? Or should I calculate at 115% service factor? Does anyone have access to info. that could explain how to read the square D heater chart? I would appreciate any assistance.