Square D QO breaker

RdmanElect

Member
Location
Poughkeepsie NY
Occupation
Electrical Contractor
If you take a look at the breaker I attached, it mentions 75degree only for #6-#2, would that mean I can't use Romex (nm cable) larger than #8 considering nm must be used at 60 degrees?
bdb6b90563a9a26271a9b87ba499bf41.jpg


Sent from my Pixel 7 using Tapatalk
 
It does seem like bad wording, but I think the intent is that #8 would be 60 degrees aluminum, or 75 degrees copper #6 to #2 rating is 75 degrees for all.
 