POCO has 8 houses on one 100kV padmoount transformer.
These houses have the same home builder and looks like the same electric sub. The oldest house in this group is 2016.
The layout to each house is POCO URD to meter & 200A panel then four wire to the 100A sub panel. The electrician’s workmanship is satisfactory and would have passed a municipal inspection.
At random times a block of four QO120DF breakers, in the panel next to each vertically, trip simultaneously. Dishwasher, disposal, washing machine and refrigerator.
Different homeowners report the same symptoms. Maybe four times in the past month. No correlation to any homeowner activities. The red herring: Homeowner #1 has a pool with a double pole GFCI breaker for the pool. When the four DF breakers trip at his house, he finds the pool breaker has tripped.
In the subpanels there are AFCI, one GFCI, another DF and two standard QO combination breakers that have not tripped when the four DFs trip. The are not 100A plug on neutral panels.
The padmount transformer was inspected, checked with a SuperBeast to force a neutral imbalance and the NEV was checked around the transformer.
Square D time saver diagnostics tripped a single DF breaker in house # 1 instantaneously.
An instant trip indicates Arcing to ground, Shared neutral, Grounded neutral or Ground fault.
A PMI voltage recorder was set at house #1 today. The recorder will be pulled after the next event.
Our history with AF, GF & DF breakers is the problems occur in new construction and usually not with QO.
I don’t see the utility power being the cause but having a common grounded conductor probably does.
These houses have the same home builder and looks like the same electric sub. The oldest house in this group is 2016.
The layout to each house is POCO URD to meter & 200A panel then four wire to the 100A sub panel. The electrician’s workmanship is satisfactory and would have passed a municipal inspection.
At random times a block of four QO120DF breakers, in the panel next to each vertically, trip simultaneously. Dishwasher, disposal, washing machine and refrigerator.
Different homeowners report the same symptoms. Maybe four times in the past month. No correlation to any homeowner activities. The red herring: Homeowner #1 has a pool with a double pole GFCI breaker for the pool. When the four DF breakers trip at his house, he finds the pool breaker has tripped.
In the subpanels there are AFCI, one GFCI, another DF and two standard QO combination breakers that have not tripped when the four DFs trip. The are not 100A plug on neutral panels.
The padmount transformer was inspected, checked with a SuperBeast to force a neutral imbalance and the NEV was checked around the transformer.
Square D time saver diagnostics tripped a single DF breaker in house # 1 instantaneously.
An instant trip indicates Arcing to ground, Shared neutral, Grounded neutral or Ground fault.
A PMI voltage recorder was set at house #1 today. The recorder will be pulled after the next event.
Our history with AF, GF & DF breakers is the problems occur in new construction and usually not with QO.
I don’t see the utility power being the cause but having a common grounded conductor probably does.