We have eight of these in the plant running vertical turbine water pumps and centrifugal blowers - Square D Class 8606 reduced voltage starters. These have been installed for about 25 years.
We have one vertical turbine pump that has trouble starting. With the load disconnected, the starter sequences to the RUN condition perfectly, time after time. Connect the pump and it usually starts stuttering about 2 seconds into a 6 second start sequence (timer relay shifts to full-voltage after 6 seconds). Same problem in HAND or AUTO.
We have replaced the contacts in 1S and 2S, the ON-delay timer, the control relay (Type XO) that activates the timer, ALL auxillary contacts on ALL contactors. We replaced the 1S and 2S coils with coils from another pump starter of the same type that started perfectly every time (and still does with the swapped coils). We have monitored coil voltages during start-up sequence on every coil in the cabinet. We have compared every voltage and resistance, including autotransformer resistances, with the pump starter that works perfectly. Everything lines up. 65% voltage during start-up is 318V, right where it should be for 490V line. We have run the 120V part of the system from a wall outlet... no change.
The motor is just back from a complete refurb - new heaters and Klixons, inspected and tested, etc. but not rewound. When the motor does start and run, it sounds normal and amps are what they should be.
After we replaced contacts in 1S and 2S, the starter was much quieter, less hum. After about six perfect starts, it started acting up again and is noisy again during the start sequence before RUN contactor pulls in. The other starter is smooth and quiet. We have opened the RUN contactor and inspected it. Nothing to see there. During the stuttering, we get small arc flashes out of the bottom of 1S (the two pole contactor).
So, according to everything we've looked at, there is nothing wrong! What are we missing???
Looking for some help! I have not found any troubleshooting info on the web.
Thanks,
Mark Elam
Rowlett Creek Wastewater Treatment Plant
Garland, TX
We have one vertical turbine pump that has trouble starting. With the load disconnected, the starter sequences to the RUN condition perfectly, time after time. Connect the pump and it usually starts stuttering about 2 seconds into a 6 second start sequence (timer relay shifts to full-voltage after 6 seconds). Same problem in HAND or AUTO.
We have replaced the contacts in 1S and 2S, the ON-delay timer, the control relay (Type XO) that activates the timer, ALL auxillary contacts on ALL contactors. We replaced the 1S and 2S coils with coils from another pump starter of the same type that started perfectly every time (and still does with the swapped coils). We have monitored coil voltages during start-up sequence on every coil in the cabinet. We have compared every voltage and resistance, including autotransformer resistances, with the pump starter that works perfectly. Everything lines up. 65% voltage during start-up is 318V, right where it should be for 490V line. We have run the 120V part of the system from a wall outlet... no change.
The motor is just back from a complete refurb - new heaters and Klixons, inspected and tested, etc. but not rewound. When the motor does start and run, it sounds normal and amps are what they should be.
After we replaced contacts in 1S and 2S, the starter was much quieter, less hum. After about six perfect starts, it started acting up again and is noisy again during the start sequence before RUN contactor pulls in. The other starter is smooth and quiet. We have opened the RUN contactor and inspected it. Nothing to see there. During the stuttering, we get small arc flashes out of the bottom of 1S (the two pole contactor).
So, according to everything we've looked at, there is nothing wrong! What are we missing???
Looking for some help! I have not found any troubleshooting info on the web.