dbehounek
Member
- Location
- Denver, CO
I have run into a problem with installation of a supply side bonding jumper in a Main service disconnect. I have a CB enclosure that is rated for use as service equipment. My inspector has failed the installation stating that I am required to have a "factory supplied" bonding jumper. This particular unit does not have provision for the green bonding screw that goes through the grounded (neutral) bus/lug kit to bond the enclosure. I sized the bonding jumper as a wire using the NEC table 250.101(C)(1) and ran the jumper from a spare lug of the neutral to a terminal that is screwed to the enclosure via tapped machine screw (1/4 x 20). The terminal bus is for the equipment ground and earth ground. I do not see a code violation here, but the ispector still fails it. Where am I wrong and what article is being sited to validate the failure of the inspection?