(My first post, apologies in advance)
I was watching: Grounding Service - Terminating grounding electrode conductor NEC Code 250.24(A)(1) by Mr. Holt. At that point in the video, he states that a supply side bonding jumper is not required between a grounded meter and the disconnect.
I
I am confused because per NEC 250.24(D) Grounding Electrode Conductor. A grounding electrode conductor shall be used to connect the equipment grounding conductors, the service-equipment enclosures, and where the system is grounded, the grounded service conductor to the grounding electrodes...
Additionally, per https://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/Article230-Services~20020219.htm the definition of service equipment is: Service equipment - The necessary equipment, usually consisting of circuit breakers or switches and fuses and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply. Service equipment does not include the metering equipment, such as the meter and/or meter enclosures [230.66].
Since we know that a grounding electrode conductor must connect the neutral conductor to a grounding electrode (at either service drop, meter or service disconnect), and a grounding electrode conductor shall be used to connect the service-equipment enclosures, how can a Neutral wire alone satisfy that requirement especially when combined with 250.24(C) Grounded Conductor brought to service equipment "...grounded conductors shall be routed with ungrounded conductors to each service disconnecting means and shall be connected to each disconnecting means grounded conductor(s) terminal or bus."
I guess I am wondering where in the code, it allows to substitute a Neutral to be used? I went to 250.142(A), (per video) and I don't see where it says this.
Any help would be appreciated.
I