In sizing the supply side bonding jumper (SSBJ) for parallel runs, table 250.102(c)(1) is now used in the 2014 NEC.
If I have 10, three phase, pvc conduit runs of (x)kcmil copper cable for a total of (10) x (x) kcmil = kcmil,
and if kcmil > 1100kcmil per table 250.1032(c)(1),
then 12.5% of this is (.125) x kcmil] = (z) kcmil,
and if (z)kcmil is > (x)kcmil
QUESTION 1:
CAN THE SSBJ BE REDUCED TO EQUAL AND NOT EXCEED THE PHASE CONDUCTORS?
QUESTION 2:
DOES THE SSBJ AS SIZED HAVE TO BE RUN IN EACH CONDUIT OR
DOES CODE ALLOW (z)kcmil TO BE DIVIDED BY THE NUMBER OF RUNS FOR THE RESULTANT (Z)kcmil / (10) = SSBJ TO BE PULLED IN EACH CONDUIT?