- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
I am confused about the nature of, and connections of, the SSBJ. The NEC has no specific definition for this phrase. Let’s start with this:
OK so far?
Now here is what I think:
NOW: This is the part I am not clear about:
So, how far off base am I?
- Utility owned transformer. Local ground rods connected to center point of WYE via GEC sized per 250.66. No N-G bond at transformer location.
- Run A, B, and C conductors from transformer X1, X2, and X3 to main breaker on service panel.
- Run N conductor from transformer X0 to neutral bar on service panel.
- Connect GEC(s) to neutral bar, and run it (them) to grounding electrode(s).
- Run "main bonding jumper" from neutral bar to ground bar inside main service panel.
- Run jumper (I don’t know what to call it - "equipment bonding jumper," perhaps?) from ground bar to enclosure of main service panel.
OK so far?
Now here is what I think:
- You need one more conductor run from transformer to main service panel.
- It is called the “Supply Side Bonding Jumper” (SSBJ).
- The SSBJ is to be sized per 250.102(C).
NOW: This is the part I am not clear about:
- I think that, at the transformer, the SSBJ is attached (essentially) to the transformer enclosure. I don’t know if there is a lug or a bar for this purpose.
- I also think that, at the main service panel, the SSBJ is attached (essentially) to the panel enclosure. I don’t know if it attaches directly to the enclosure or to the ground bar.
- Are these the correct connection points?
- One final point: I think the only reason for the SSBJ is to provide a path for clearing a fault that takes place at the transformer, from a hot conductor to the enclosure. The fault path is as follows:
- A fault connection occurs between X1 (or a point downstream, but still internal to the transformer) and the enclosure.
- If there is no SSBJ, the enclosure would be energized but no current would flow.
- With the SSBJ routed as described above, current would flow from the fault point to the SSBJ connection, along the SSBJ to the main service panel enclosure, to the ground bar, to the neutral bar, along the neutral conductor back to the center point of the WYE, thus completing the circuit.
- There will be sufficient current flowing along this path to activate the primary side overcurrent device.
So, how far off base am I?