SSBJ vs EGC for parallel runs

Status
Not open for further replies.
Great question, I have no idea. IMO the SSBJ rule should apply to all parallel runs even when using an EGC.
 
LOL! Yeah the EGC gets me. I can use a metal raceway as an EGC but as soon as I stick a wire type EGC in there it must be full sized in each parallel raceway.
 
Great question, I have no idea. IMO the SSBJ rule should apply to all parallel runs even when using an EGC.

You may get your wish.

There are several Public Inputs that have been submitted for the 2020 NEC that would radically change Table 250.122. The Public Inputs would change the table from basing the size of the EGC on the OCPD to sizing the EGC based on the size of the ungrounded conductors similar to Table 250.102(C).

I have a couple of friends on CMP 5 and this idea has some backing. It will be interesting to see where the PI goes in a few weeks at the First Draft Meeting in January.

Chris
 
You may get your wish.

There are several Public Inputs that have been submitted for the 2020 NEC that would radically change Table 250.122. The Public Inputs would change the table from basing the size of the EGC on the OCPD to sizing the EGC based on the size of the ungrounded conductors similar to Table 250.102(C).

I have a couple of friends on CMP 5 and this idea has some backing. It will be interesting to see where the PI goes in a few weeks at the First Draft Meeting in January.

Chris

That's good news. I believe that our moderator Don has submitted several proposals across many code cycles to do just that, base the EGC on the size of the conductors, but each time he was rejected.
 
You may get your wish.

There are several Public Inputs that have been submitted for the 2020 NEC that would radically change Table 250.122. The Public Inputs would change the table from basing the size of the EGC on the OCPD to sizing the EGC based on the size of the ungrounded conductors similar to Table 250.102(C).

I have a couple of friends on CMP 5 and this idea has some backing. It will be interesting to see where the PI goes in a few weeks at the First Draft Meeting in January.

Chris

That would be nice. But note sizing based on the area of the ungrounded conductors is different than requiring a full sized in each raceway. Does the discussion for the change encompass the latter too?
 