How come an EGC run with parallel runs for a feeder needs to be full size in each pipe , but we don't need full size in each pipe for the SSBJ on a SDS?
Great question, I have no idea. IMO the SSBJ rule should apply to all parallel runs even when using an EGC.
You may get your wish.
There are several Public Inputs that have been submitted for the 2020 NEC that would radically change Table 250.122. The Public Inputs would change the table from basing the size of the EGC on the OCPD to sizing the EGC based on the size of the ungrounded conductors similar to Table 250.102(C).
I have a couple of friends on CMP 5 and this idea has some backing. It will be interesting to see where the PI goes in a few weeks at the First Draft Meeting in January.