We designed and built a custom control panel labeled at 10ka per UL508a. All the power devices in panel are actually rated at 65ka, but since we used a distribution block, panel could only carry 10ka rating. Now panel is at installation and it is discovered that available fault current is 25ka.
Would it be acceptable to install a fused disconnect ahead of panel with current limiting fuses having a peak let through current of less than 10ka @ 25ka?
Would it be acceptable to install a fused disconnect ahead of panel with current limiting fuses having a peak let through current of less than 10ka @ 25ka?