Ref SSR vs Mechanical thread. I did a small shop experiment. I removed power at the start of each lamp change. Electric unit heaters may have cycled at some time during test.
Voltage = 124.9 Control is SSR 12vdc
ssr 60 w Lamp
L|-------][--------------------INC-------------|N
Apply L-N=124.9
Open Ssr=124.9 Lamp=.78mv
Closed Ssr =1.18 Lamp=123.9 (On)
Open Ssr=124.4 Lamp=.94 & going down (Off)
Removed all power, changed Lamp to 60 watt LED non dimmable
Apply L-N=124.9
Open Ssr=86 Lamp=40
Closed Ssr=1.02 Lamp=123.7 (On)
Open Ssr=86 Lamp=40 (Off)
Remove all power, changed lamp to 5.5 watt LED dimmable
Apply L-N=124.7
Open Ssr=122.7 Lamp=7.06
Closed Ssr=1.4 Lamp=124 (On)
Open Ssr=31.9 Lamp=103.8 (On, dim)
My question is where did the increased 11 volts come from ? (No, not a neutral issue)